Horuce info zo Studeru ohladom noveho updatu R677:
The new software version include parameter
"{6075} Max SOC for end of charge" and further improvements we will share in a news as soon as test will be released.
Addition of a maximum SOC to stop charging defined by the user:So far, the system charged the battery until the BMS required to reduce the
charging current and the battery reaches 100% SOC. However, many
customers wanted to add a limitation in the maximum SOC on the battery.
In that way, they could decide to limit the maximum charge level as this can
be beneficial for the battery lifetime.
A new parameter “Maximum SOC for end of charge” {6075} is added in this
software release. No charger will exceed to value.
The %SOC limitation was already possible in some cases with the “SOC for
backup {6062}” and “SOC for grid feeding {6063}” parameters when the
Xtenders were charging from an AC source (grid or generator). However, in
island mode those parameters were not used, reason why we had to include
this new parameter {6075} to also limit the charging when working only with
the solar chargers.
image (2).png
Notes: o The storage buffer between SOC for backup and SOC for end of charge can be used to supply the load with solar priority function {6071}. The solar priority and the grid-feeding must not be activated at the same time: either your use your energy only for your load, or you inject all the excess and it goes to the load or the grid.