ModbusRtu/10/params/
Parameters for inverter INVSOL01 - AC,Bat,PSQ,Freqv,Temp
7.10.2023*16:58:45
Protocol:Rtu
Description:Protocol for INVSOL01 Modbus RTU 1.01.15
Device:INVSOL01,USB-RS485
Port:Com,5,19200,8,1,0
Timing:Timer=10,Sleep=10,Wait=200,Timeout=5
Device Address:04
Commands:24
001:0x03,0x62,0x75,0x00,0x01/1,0,99999,1.0/V,Battery voltage 0.1V
002:0x03,0x62,0x76,0x00,0x01/1,0,99999,1.0/V,Inverter voltage 0.1V
003:0x03,0x62,0x77,0x00,0x01/1,0,99999,1.0/V,Grid voltage 0.1V
004:0x03,0x62,0x79,0x00,0x01/1,0,99999,1.0/A,Control current 0.1A
005:0x03,0x62,0x7A,0x00,0x01/1,0,99999,1.0/A,Inverter current 0.1A
006:0x03,0x62,0x7B,0x00,0x01/1,0,99999,1.0/A,Grid current 0.1A
007:0x03,0x62,0x7C,0x00,0x01/1,0,99999,1.0/A,Load current 0.1A
008:0x03,0x62,0x7D,0x00,0x01/1,0,99999,1.0/W,PInverter 1W
009:0x03,0x62,0x7E,0x00,0x01/1,0,99999,1.0/W,PGrid 1W
010:0x03,0x62,0x7F,0x00,0x01/1,0,99999,1.0/W,PLoad 1W
011:0x03,0x62,0x80,0x00,0x01/1,0,99999,1.0/%,Load percent
012:0x03,0x62,0x81,0x00,0x01/1,0,99999,1.0/VA,SInverter 1VA
013:0x03,0x62,0x82,0x00,0x01/1,0,99999,1.0/VA,SGrid 1VA
014:0x03,0x62,0x83,0x00,0x01/1,0,99999,1.0/VA,Sload 1VA
015:0x03,0x62,0x85,0x00,0x01/1,0,99999,1.0/VAr,Qinverter 1var
016:0x03,0x62,0x86,0x00,0x01/1,0,99999,1.0/VAr,Qgrid 1var
017:0x03,0x62,0x87,0x00,0x01/1,0,99999,1.0/VAr,Qload 1var
018:0x03,0x62,0x89,0x00,0x01/1,0,99999,1.0/Hz,Inverter frequency 0.01Hz
019:0x03,0x62,0x8A,0x00,0x01/1,0,99999,1.0/Hz,Grid frequency 0.01Hz
020:0x03,0x62,0x91,0x00,0x01/1,0,99999,1.0/oC,AC radiator temperature
021:0x03,0x62,0x93,0x00,0x01/1,0,99999,1.0/oC,DC radiator temperature
022:0x03,0x62,0xB9,0x00,0x01/1,0,99999,1.0/W,Batt power W
023:0x03,0x62,0xBA,0x00,0x01/1,0,99999,1.0/A,Batt current A
024:0x03,0x62,0x78,0x00,0x01/1,0,99999,1.0/V,BUS voltage 0.1V
end